Thanks for that, am I right in thinking those figures may relate toTbh my rule of thumb (engineers) 14-30 rads 25-80 under 15-60
Yes pump definitely stats powered up and all heating controls / valves are functioning correctly tooSomething very strange going on, assuming boiler flow temp set to 70C then when the burner cuts out with a return temp of 25C means that you are only circulating 6LPM (0.36M3/hr) which equates to the 38W pump output you mentioned previously.
A running time of 37.5% is a average output of 7.5kw with a 20kw boiler or 9.75kw with a 26kw.
Can/have you checked that the circ pump stays running when the burner cuts out.
Thanks for that, am I right in thinking those figures may relate to
25mm inlet
80mm pump vane?
If so yes that would make sense as old units are 15mm inlet and 60mm vanes
Could you freeze one side and adjust the pipe/ pump valve sages draining down ?
Is the boiler firing or not with that temp of 89.5C?.Upstairs has been running on its own tonight for a couple hours. 2 double rads hot and bathroom tall single hot.
On time = 1.5 mins. Off time= 4 mins 45 secs.
Return temp 43c
View attachment 67200
View attachment 67201
Again on the small upstairs zone I can get all rads warm. But when I balance first 2 correctly the rest fall off cold even with valves fully open.
It's on the larger downstairs circuit that the return temp never rises above 25c even after hours of running.
Is the boiler firing or not with that temp of 89.5C?
I think the max boiler setpoint temp on that boiler is 75C or maybe just 80C max?. Can you ensure that the pump is pumping away from the boiler and what is the power showing there, it looks like 13W? What is the boiler stat set to? there is a 28mm? copper elbow under the boiler stat, is that the vent?.
Thanks, that very high temp of 89C might cause the pump to cavitate and cause circulation problems, might try a SP of ~ 70C for tomorrow and see what the pump power is. Can you see what that power reading was above, looks like 13W to me.
OK thanks again, can see tomorrow what the 70C does, if anything, you will soon know as the boiler dT will decrease if the pump is circulating more.
Presume boiler only ran continuously for 20 minutes or so and then started cycling??.