Yes I plumbed the stove in about 5 years ago. It is absolutely safe I made sure of that hence why I wanted to do it myself. Eg, large capacity gravity rad which was sized per manual to soak away the heat if fhe power went out in use and heating not circulating. In conjunction with high and low pipe stats and a thermostatic damper on the stoce which at that time was special order. (Now it is legal requirement as I understand it and all new stoves should come with it.
But... here is an update. When I changed the ball cock in heating tank I noted it was too high. Set about 2 inches below the outlet.
So the new ball cock heating tank level is only a couple inches above the outlet to allow for expansion.
So that was yet another error in the system.
But the main error it appears when I thought about it is the actual vent pipe itself. This house has the old school heating plumbing whereby if you wanted hot water it switched the boiler on and no pump hence it raised up the pipe and fell back down warming the cylinder coil.
That is a 22mm pipe which goes from the boiler and loops over and down into the hot press. With a 15mm vent pipe teed off that mid point and above heating tank.
Years ago when I was upgrading the controls in the house I may have made an error of judgement 🙄 I fitted a cylinder stat and control valve to the hotpress 22mm pipe.
I was thinking about this and did a test there by turning on hot water to permanent on (I normally use economy 7 electric on immersion heater all year around) and switch heating on and off.
Bingo- now the heating tank water level stays AOK doesn't rise. Sits at correct level. Could be speaking too soon but before I opened that it was pumping up and out the overflow then filling back up again a little when shut down. Now it stays level. Will it creep up still? Time will tell.
I guess this is just how the house was plumbed and I need to remove that valve, the only downside being that there will always be a degree of hot water from normal space heating running but that's OK.