Thanks for the replies.
Bunker the rads both upstairs and downstairs all heat up to temp in 20 mins,
About right.
If I turn the boiler stat down it comes up to temp quicker then short cycles, if I turn up the boiler stat it takes a bit longer to get to temp then short cycles.
Reads exactly the opposite to what I would expect, what controls your boiler firing?
If I go from a 0.65 to a 0.4 I will reduce my gph by 37% rather than halving it as you mentioned.
Riellos spec sheet for my burner says you can run between a 0.4 and a 0.65 nozzle with the same pump pressure.
Riello manufactured the burner not the boiler, it is the boiler manufacturer who spends the big money on R & D to ensure the correct burner, nozzle and settings are used to achieve the most efficient performance.
Lame plumber, if you re-read my posts I have always used a registered engineer, hence my issues!.
Peteheat, thanks again for your comments.
As mentioned I will get a stack temp ,co2 etc analysis done for sure.
What I object to is paying hundreds of pounds a year for an engineer not to service my boiler properly.
Far as I know from earlier posts I'm probably one of the most expensive service engineers who posts here, allowing for currency exchange rates I would be charging circa £100.00 for an oil boiler service.
I want my customers back again next year so if there is a problem with a job I do I want to know about it, I understand most who post here have a similar policy.
With respect I suggest you use a new service engineer / technician preferably one with a plumbing back ground.
I am quite capable off scraping crap off the inside of my boiler if the engineer doesn't
I have found nozzle containers that vary from 0.4 to 0.65 in the case of my boiler.
The burner can use nozzles in that range, that does not mean they suit the boiler in fact .65 is only part of the nozzle data.
I think my'engineer' has put bigger nozzles in over the years to combat the inefficient coked up chamber.
Best, thanks for your reply,
The boiler is sited in the downstairs toilet with a rad in it.No underground pipes
Most of the rads are singles and little.
I have no need to run the hw tank and the rads at the same time.
Cheers
Craig
You mention in a later post that it is now taking a continuous 80 minutes to achieve the same temperature the larger nozzle achieved in 20 minutes, the basic maths should be telling you all the advice you received was correct, you are using more oil with the smaller nozzle.
To answer your last question, the cycle time should be directly related to the heat loss of the building.
Nobody is calling you stupid we are trying to help by posting a few lines (I touch type with one finger) after we have completed a fairly hard days work, it is not always possible to trouble shoot a boiler problem without being in front of it.
Sorry I can't be of more help.