It would go round the LLH. That's effectively your bypass, plus an integrated one.If there was no circuit you wouldn't of had flow. Did you have a bypass?
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Pump overrun is killing my heating! in the Central Heating Forum area at Plumbers Forums
It would go round the LLH. That's effectively your bypass, plus an integrated one.If there was no circuit you wouldn't of had flow. Did you have a bypass?
The only bypass is the one in the boiler.If there was no circuit you wouldn't of had flow. Did you have a bypass?
It would go round the LLH. That's effectively your bypass, plus an integrated one.
There is a bypass in the boiler, but yeah the Vaillant controls usually hold the zone valve open for a period of time. Well they do on the newer system from what I recall.
Yes, in the new setup it can cycle to the LLH and back. If the external pump was on, it could cycle further (and cool down quicker, while at the same time continuing to provide heat - to the cylinder in the morning) and I guess this is the crux of the issue that this doesn't happen in pump overrun mode.It would go round the LLH. That's effectively your bypass, plus an integrated one.
Yes, there's definitely power as the LEDs are on and I can feel the pump vibrating, which increases as I increase the speed.Out of interest have you checked to see if there's power to the pump? I've had a couple of them newer UPM3s fail quite early on tbh.
I meant when it isn't running and the boiler is saying it should be.Yes, there's definitely power as the LEDs are on and I can feel the pump vibrating, which increases as I increase the speed.
Ah, sorry, I see what you mean.I meant when it isn't running and the boiler is saying it should be.
Ah right OK, as I said in an earlier post then i'd configure your HW configuration correctly on the PCB first and see if that makes a difference. You're probably getting a lot of anti cycling.Ah, sorry, I see what you mean.
The only situations I'm aware of where the external pump doesn't start, when the internal pump does start is S.0 and S.7. It is possible there are other status codes that I haven't come across, but these are the two I regularly see.
However, when there's demand and neither of the above status codes are showing on the boiler, then both pumps are on at the same time.
Can I just ask, who did that drawing for you? It's great, I struggle to get an answer for basic things out of my rep (Although he isn't bad to be fair).Yes, the system has always been setup for DHW priority.
D.75 = 45 (factory setting)
D.77 = 37 (factory default and maximum output I believe)
D.78 = 80 (factory default)
So, it looks like these settings are all defaults.
Yes, the cylinder temperature probe has been connected to S9 on the VR 71 wiring centre as shown in the attached schema diagram. This diagram was supplied by Vaillant as the nearest to my setup as none of the diagrams in the VRC 700 System Diagrams booklet were any good! However, this diagram shows each zone has having its own pump (and mixing valve), which isn't the case in my system.
I don't think Vaillant created that drawing especially for me. If you look at the date, it is 30/07/2018.Can I just ask, who did that drawing for you? It's great, I struggle to get an answer for basic things out of my rep (Although he isn't bad to be fair).
Should be down as external pump I think.Just found the installation guide for the X40 expansion board, which plugs into the boiler PCB and provides for the external pump connection.
Here are the relevant pages:
View attachment 46989
View attachment 46991
I'm trying to understand how the above relates to the actual device and the way the pump has been wired upto it:
View attachment 46990
On the boiler d.27 = 5 and d.28 = 2
What's the difference between "Circulation pump", "External Pump" and "Storage charging pump"?
Based on the photo, showing the pump is connected to the yellow "rel 1" connectors, which 1, 2, 3, 4, 5 or 6 does this relate to?
Because it is wired to rel 1 (open) and d.28 is 2, I assume it relates to 2 in the table. Are 1 and 2 mutually exclusive. 1 shows a ZP & tap and 2 shows a radiator, so I'm thinking they relate to DHW and heating! I'm not sure what "ZP" means.
Note: Just realised the last paragraph is nonesense as d.28 relates to "rel 2", so I'm now wondering if either the connection is wrong or the setting of d.27 is wrong!
So, assuming external pump is correct, does the chart suggest it can be wired in either of two different ways:Should be down as external pump I think.
Shaun, are you saying the LED's on the pump would still work even if the pump didn't have power? When I press the speed button on the front of the pump, I can hear/feel the pump toggling through the different speeds. Also, if the pump wasn't working, surely the radiators/UFH and hot water would never warm up as there's no way the internal boiler pump could push water past the LLH and around the system!Also don’t forget about if there’s flow through the pump the leds will light up as the unit is acting like a generator eg there’s no power going to the pump plug
Given my comments above about the pump and the fact that I've done tests on each thermostat to force demand for each zone and can see the pump LED's turning on/off as demand is requested/removed, I'm feeling very confident the external pump is working. Whether it is connected and configured correctly is another matter!Also S.0 refers to "no heating demand" which I would think is indicative of the boiler sensing no heat demand even with zone valve(s) open, I would have a good look at that Grundfos Pump as it may be the main cause of your problem, hopefully.
So, I set the heating and hot water to start at 06:30am this morning, which is half an hour later than I usually set it, but I wanted to monitor what happened. At 07:00am the system was still heating the cylinder. The external pump was on, the system status (via the VRC 700) was showing DHW and the boiler status was S.24 (Burner ignited), so all looked to be okay, apart from that fact that the cylinder was still not to temperature (65 degrees C) after 30 minutes. There was absolutely no heat in the radiators or UFH.Following this very interesting thread.
Just a few basic observations.
Pump overrun should not occur unless CH and/or HW satisfied, if boiler output still too high on max turndown then burner off but boiler circ pump and secondary pump should continue to run but overrun should not be called for. When pump overrun is called for normally, would expect secondary pump to be off. Suggest to check if pump overrun comes on with burner off with call from CH or HW.
Slow rad heat up/output not mentioned but with a LLH the boiler circ pump and external pump should be matched with boiler circ pump flowrate slightly higher?. so possibly wrong settings with boiler circ pump or more likely secondary pump or faulty pump. Also assume LLH connections correct.
Sorry, I meant to comment on your post.Following this very interesting thread.
Just a few basic observations.
Pump overrun should not occur unless CH and/or HW satisfied, if boiler output still too high on max turndown then burner off but boiler circ pump and secondary pump should continue to run but overrun should not be called for. When pump overrun is called for normally, would expect secondary pump to be off. Suggest to check if pump overrun comes on with burner off with call from CH or HW.
Slow rad heat up/output not mentioned but with a LLH the boiler circ pump and external pump should be matched with boiler circ pump flowrate slightly higher?. so possibly wrong settings with boiler circ pump or more likely secondary pump or faulty pump. Also assume LLH connections correct.
Do you mean set the timer to stagger the start times for hot water and heating, so:What happens if you set the water to run more than an hour before the heating comes on? i.e. allow the water to run and then turn off before running the heating?