@milleniumaire, have you noted the flow/return temps with HW heating on?,
@EvilDrPorkChop says 80C flow temp, also I think the cylinder temp is set in the controller and not on the boiler front, maybe the boiler front acts as a max limiter. There is also reference to pump overrun in the controller manual which would seem to state that pump overrun will take place for a limited period once the cylinder reaches temperature (with the zone valve opened) and the "charging" pump running, there seems to be a 10 min overrun time judging by the 10 min delay between HW off @ 0700 and CH on @ 0710, whatever about the "charging" pump run status.
Hi guys, I did some checking of temps this morning as requested. The system (heating and hot water) started at 06:30am and I checked it at 07:10am. It was still in DHW mode, trying to heat up the cylinder.
The analogue pipe thermostats showed:
Boiler flow to LLH: 68
Boiler return from LLH: 63
LLH flow to system: 68
LLH return from system: 60
On the VRC 700, I could see the following temperatures shown:
DHW current flow temp: 79
System flow temp: 76
DHW Target flow temp: 90
Domestic host water: 65
Current temp: 63
Cyl. temp top: 73
Cyl. temp bottom: ---
In the DHW menu, I also noticed the following settings:
Max. cyl. charg. time: 60 min.
DHW req. anti cy time: 60 min.
Ch. pump overrun time: 5 min
Parallel cyl. charging: off
It would appear the reason I'm seeing the heating start to come on an hour after it has started is due to the "Max. cyl. charg. time" setting of 60 mins? So, even after an hour the cylinder isn't reaching 65 deg C, but then switches to heating mode due to this setting. Not sure of the impact of the other DHW settings.
Last night, I happened to catch the boiler showing S.7 (pump overrun). The external pump was off, but it showed the internal pump was on and there was a DHW demand. My son had recently had a shower. While I watched it, the S.7 changed to S.0 (no demand). I can't say how long it had been at S.7, but I did notice the radiators were luke warm, so suspect the DHW demand had been running for some time.
Right now, 3 hours after starting, the system is in Heat mode, DHW target flow temp is showing 0 and DHW current temp is showing 65, so clearly it has eventually reached the required hot water temperature.
As suggested, I think I will turn the boiler temperature down to 60 deg C and see what impact that has in the morning. Just need to figure out if it should be turned down using the boiler dial or the VRC 700. I'll probably do both, just to be sure!
Yesterday, I emailed a bunch of questions off to Vaillant, including details of how the Grundfos pump was connected/configured and how long they would expect it to take for the cylinder to heat up, with examples of the current settings in the hope they might see something that needs to be changed.