ive worked it out as you say and I get this, which tbf isn't goin to make much difference and is also going the rite way aslong is doesn't exceed the maximum permisable volume per hour.

8m of 35mm @ 0.00084 pm
7m of 22mm @ 0.00032 pm
12m of 15mm @ 0.00014 pm

8 x 0.00084 = 0.00672 m3
7 x 0.00032 = 0.00224 m3
12 x 0.00014 = 0.00168 m3

total pipe work = 0.1072 m3

meter (u6) 0.008 m3

total of meter and pipework = 0.01864 m3

+ 10% =0.001864 m3

total instantiation = 0.020504 m3

Right
 
if a zero governor actually pulls the gas through could that not lead to problems with other appliances if it overpulled or even lock up the meter regulator?
 
yeah I do have a viper im resitting so it is a few years out of date probably, the tightness test is a bit different to when I went through this last time il have a look in there see what it says
 
if a zero governor actually pulls the gas through could that not lead to problems with other appliances if it overpulled or even lock up the meter regulator?

yes and no

if pipwork is sized correctly no as it will have the required amount of gas so wont pull from other appliances

yes if the pipework is too small / distance is too great for 15mm/22mm etc
 
yeah I do have a viper im resitting so it is a few years out of date probably, the tightness test is a bit different to when I went through this last time il have a look in there see what it says

have a look at H6
 
Yeah it doesnt include the meter in my book ...think that means its out of date on this?

20151025_194126.jpg
 
Yeah it doesnt include the meter in my book ...think that means its out of date on this?

View attachment 23555

no your right the formulas wrong in your first post should read

installation volume in cu meters = Vm + (Vp + Vf) = inst v

sorry about that will work it out again

image1.jpg

same as mine but you have the fancy colour version
 
Last edited:
one less thing to worry about cheers

8m of 35mm @ 0.00084 pm
7m of 22mm @ 0.00032 pm
12m of 15mm @ 0.00014 pm

8 x 0.00084 = 0.00672
7 x 0.00032 = 0.00224
12 x 0.00014 = 0.00168

total pipe work volume = 0.01064 m3

+ 10% = 0.001064 m3

Pipework volume + 10% = 0.011704

meter (U6) 0.008 m3

total of meter and pipework volume = 0.019704 m3

total installation volume = 0.019704m3
 
nice one that looks like what I got now....sorry to be a pain but do you have any advice on unsafe situations? I find it a nightmare distinguishing between AR ID and NCS? is there like a rule of thumb? as an example one mock question was ...You see a scorch mark on a carpet below a radiant gas fire how would you classify the situation? I put ID as at any time it could set the carpet alight but the tutor said its AR which surprised me.
 
nice one that looks like what I got now....sorry to be a pain but do you have any advice on unsafe situations? I find it a nightmare distinguishing between AR ID and NCS? is there like a rule of thumb? as an example one mock question was ...You see a scorch mark on a carpet below a radiant gas fire how would you classify the situation? I put ID as at any time it could set the carpet alight but the tutor said its AR which surprised me.

the carpet is only at risk of going on fire,
your thinking of spilling thats id easy way anything to do with fluing or on old boilers case seals id
 
New posts
Status
Not open for further replies.

Similar plumbing topics

Set whatever boiler you're installing to the...
Replies
2
Views
922
Ok I think I see what your saying mate, So...
Replies
9
Views
1K
LPG lock up pressure can be regarded as the...
Replies
4
Views
1K
Hi Boilermedic can help you with your...
Replies
7
Views
2K
Yeah done a couple during the 2 years training...
Replies
6
Views
949
Back
Top