Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Trainee gas questions in this thread ONLY please in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
what are you opinions about the flame picture here? is the orange caused by dust/dirt?



IMG_20140328_210055.jpg
 
Flame looks blue and radiants hot. On my phone. Normally dust results in soot. What was the bp ?
 
Just a wild card tip here lads and lasses. Keep your Facebook profile sensible. We just sacked a lad off( didn't even start his first day) as his Facebook was all about smoking weed and getting up to mischief. Sorry .
 
Just a wild card tip here lads and lasses. Keep your Facebook profile sensible. We just sacked a lad off( didn't even start his first day) as his Facebook was all about smoking weed and getting up to mischief. Sorry .

Have to say, schoolboy error in this day and age
 
another quick question.

just need some clarification please.

When pipe sizing, i know that you are allowed 1mb drop in pressure. Does this mean the drop is allowed per appliance. for example, 1mb drop on boiler, then another 1mb drop on hob or is the 1mb drop permissible as a whole? hope that makes sense....
 
hi all,
I've not logged in for a while..been really busy completing my portfolio which has now been finally signed off.

I'm just revising to sit my exams.

I've come across few questions on gas rate and heat input which has got my stumped...i just cannot seem get the correct answers. by using the method i've been taught to calculate.

any help in showing the calculations would be much appreciated so i know where i'm going wrong:

Assume the following specification for the questions which follow:Metric CVgross (nat.gas) = 38.76 MJ/m3
Imperial CVgross (nat.gas) = 1040 btu/ft3



The Index of a U16 meter is showing a reading of 60.00 then 2 minutes and 24 seconds later it is showing 60.18 during which time a large domestic boiler was operating. What is the heat Input of the boiler?


I. 4.85 kWnet.
II. 28.06 kW net.
ii. 43.65 kW net.
iv. 48.45 kW net.


A natural gas fire is operating at full rate and timed for a period of 2 minutes ans 3 seconds. The G4 meter index starts at 00001.230 and ends at 00001.249 during this period. What is the heat input of this appliance?



i. 3.268 kWnet
ii. 3.628 kWnet
iii. 5.394 kWnet
iv. 5.987 kWnet

The index of an E6 meter is showing a reading of 26942.987 and again 2 minutes and 5 seconds later during it's showing 26943.053 which time a combi boiler was operating on hot water. What is the heat input of the boiler?



i. 11.24 kW net.
ii. 12.48 kW net.
iii. 18.44 kW net.
iv. 20.4 7 kW net
 
Last edited:
ok, i've figured out the first 2...if anyone is interested, here's what i did:

0.18 x 3600 = 648
648 / 144 seconds = 4.5
4.5 x 38.76 = 174.42
174.42 / 3.6 = 48.45kw

0.019 x 3600 = 68.4
68.4 / 123 = 0.55
0.55 x 38.76 = 21.55
21.55 / 3.6 = 5.98kw


i'm still struggling with the last one through..........
 
Hey all,
I've got my exams in 2 weeks time.

i would appreciate any pointers as to what I can expect for the practical exam. what will i be expected to know and which tasks to carry out?


:)
 
Hey all,
I've got my exams in 2 weeks time.

i would appreciate any pointers as to what I can expect for the practical exam. what will i be expected to know and which tasks to carry out?


:)

Tightness test, gas rating appliances, service a fire, fault find a cooker, fault find a section of pipework, vents and flues, name a load of controls on a board. Service a water heater errrrrrrr mm I'll think of some more :)
 
The last question is 20.47 I think. I just work it out to 2 minutes and go a fraction higher :)courtesy of the mr combi gas rate app :)
na6eve6a.jpg
 
Last edited:
Read bs5440 and just know where to find stuff. Few questions of flues
 
Thank you Chris and Ermintrude.

Chris, i worked out the calculations for the last question:

The index of an E6 meter is showing a reading of 26942.987 and again 2 minutes and 5 seconds later during it's showing 26943.053 which time a combi boiler was operating on hot water. What is the heat input of the boiler?

26943.053 - 26942.987 = 0.066
0.066 x 3600 = 237.6

237.6 / 125 seconds = 1.9008

1.9008 x 38.76 = 73.675008

73.675008 / 3.6 = 20.46528

For any other trainees who are reading this, the values in red at constant...
 
Thank you Chris and Ermintrude.

Chris, i worked out the calculations for the last question:

The index of an E6 meter is showing a reading of 26942.987 and again 2 minutes and 5 seconds later during it's showing 26943.053 which time a combi boiler was operating on hot water. What is the heat input of the boiler?

26943.053 - 26942.987 = 0.066
0.066 x 3600 = 237.6

237.6 / 125 seconds = 1.9008

1.9008 x 38.76 = 73.675008

73.675008 / 3.6 = 20.46528

For any other trainees who are reading this, the values in red at constant...

Well done mate :)
 
Hello All,
another quickie..

I'm struggling a little with understanding downstream and upstream when it comes to placement of fans on boilers.

can someone please explain to a complete idiot which one if downstream/upstream from the image and why...




flue-types.jpg

Also, when it comes to upstream of gas meter, does it this mean flow of gas before the meter or after..... :thinking:
 
See it as the way a river flows.

Its the travel direction of the gas or gasses in this case
Up is where it's coming from.
Down is where its going.


Fans upstream of the heat exchanger will be positive pressure.
And downstream negative pressure.

Ultimately see upstream (oil/gas exploration) and downstream as consumer/end user
 
In this order

Natural draught
Downstream
Upstream
Downstrean


In the diagram instances the reference is in relation to the position fan to the burner
 
Last edited by a moderator:
Status
Not open for further replies.

Similar plumbing topics

Thank you for the detailed and considered...
Replies
14
Views
1K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
857
HRP123
H
Hi RPM, Gasway were the first company i...
Replies
4
Views
2K
I personally use these to do pipesizing calcs.
2
Replies
25
Views
8K
Back
Top