- Messages
- 146
You are very knowledgeable. Thank you.Yes, but there are lots of ways of skinning a cat, if the kitchen has a cycle time of 3hrs, 1 hr on time so kitchen average requirement is 21.85x0.33=8.3kw, ideally the UFH should give this output continuously and the manifold output can be reduced by various means, reducing the mixing temperature for example so assuming Laundry similar at 11.5x0.33=3.8kw, then continuous UFH demand is ~ 12.1kw, the rads might cycle in a similar fashion, so you may well find that 35kw output is quite sufficient.? You measured your oil consumption at ~ 23LPD or ~ 10kwh/hr so not a mile away from the above?.
Ok so heres what I think I need to do from our conversations:
- Reinstall original pump
- Install another EV
- Turn TMV down on kitchen manifold
- Install new pump set on Laundry manifold
- Upsize boiler back to 35kw
- Replace blast tube to correct one, as per instruction manual
- Install bypass?
And hopefully we will have a system the will operate efficiently.