If you are referring to the 18L (white) EV, it appears to be connected to the Cylinder cold water inlet? (with blue isol valve), post #87.
 
Another question, I have watched the pump running on both the kitchen (troubled) and laundry manifolds, individually. Correct me if I’m wrong but should the kitchen manifold not run at less RPM than the laundry manifold that had 50m flow and return pipe? The kitchen manifold runs in 32mm cooper from boiler (5m) until it tees off for manifold then it runs in composite 26mm for 2 metres till it joins manifold.

Doesn’t the boiler pump only control the flow and return from the manifold and the manifold pump controls the flow and return in the manifold circuits?

Ok will do thanks John. You said in a previous post the boiler pump is normally around .4 bar, 4m head, if this external pump is set to 1.35 bar 13.5m head is this an issue with the expansion vessel, as the expansion vessel charged to one bar allows the system a static head of 5m. View attachment 76721
Will reply to manifold pump later.

Re boiler external pump, if the EV is connected into the suction side of the pump, the pump discharge pressure should be the EV pressure+the pump head, in your case, 1.3bar+1.35bar=2.65bar, if the EV is connected at the pump discharge then the pump discharge pressure will be the same as the EV pressure, in your case. 1.3bar, the pump suction should then be the EV pressure-the pump head, 1.3bar-1.35bar=minus 0.05bar or minus 0.5M which means part of the system can be running under negative pressure, not desirable as air can be drawn in, in practice boilers (especially Gas) often have their EVs connected into the discharge side but with a EV pressure of 1.3bar and a pump head of say 0.7bar will still result in a positive pressure at the suction side, 1.3bar-0.7bar=0.7bar or 7M.
 
If you are referring to the 18L (white) EV, it appears to be connected to the Cylinder cold water inlet? (with blue isol valve), post #87.

Yes not cold inlet coil, cold is below
 
Will reply to manifold pump later.

Re boiler external pump, if the EV is connected into the suction side of the pump, the pump discharge pressure should be the EV pressure+the pump head, in your case, 1.3bar+1.35bar=2.65bar, if the EV is connected at the pump discharge then the pump discharge pressure will be the same as the EV pressure, in your case. 1.3bar, the pump suction should then be the EV pressure-the pump head, 1.3bar-1.35bar=minus 0.05bar or minus 0.5M which means part of the system can be running under negative pressure, not desirable as air can be drawn in, in practice boilers (especially Gas) often have their EVs connected into the discharge side but with a EV pressure of 1.3bar and a pump head of say 0.7bar will still result in a positive pressure at the suction side, 1.3bar-0.7bar=0.7bar or 7M.
IMG_9383.jpg
The EV connects into the firebox, I guess you would say its on the suction side the pump? is 2.65 bar discharge not to high?
 

Attachments

  • tempImageXPIFmm.png
    tempImageXPIFmm.png
    4.4 MB · Views: 42
Its may cause erratic operation of the UFH manifold TMV because you have hot water at high pressure on one side of the TMV and much lower pressure on the other side coming from the cold manifold return.
 
I think that's what's happening, i just can't work out why the pump is running so fast to circulate water around the closest circuit to the boiler. I'm stumped :))

Below pics of pump operating different circuits, notice the ktichen manifold RPM compared to laundry and Radiators that have a longer circuit.

Also done an experiment with rads and kitchen (troubled manifold) both calling for heat, boiler flow never got over 43.6 degrees after 40 mins of running, i turned ufh manifold off and within 2.39 mins flow temp had risen 13.4 degrees to 57.

I am now thinking if the pump if pushing water that fast through flow to manifold is this indicating a blockage in the flow pipe?


IMG_9364.jpg



IMG_9393.jpg
IMG_9413.jpg
Its may cause erratic operation of the UFH manifold TMV because you have hot water at high pressure on one side of the TMV and much lower pressure on the other side coming from the cold manifold return.
 
Can you give me your observed/estimated readings for the two UFH manifolds, ie, boiler/manifold flow temp, manifold(s) flow (mixed) temps & return temps & the total manifold flow rates.
Also a rough idea of the total rated rads output and the actual/estimated dT.

Does that pump display only the RPM in that box?, ie some can display the calculated flowrate if selected.
 
Can you give me your observed/estimated readings for the two UFH manifolds, ie, boiler/manifold flow temp, manifold(s) flow (mixed) temps & return temps & the total manifold flow rates.
Also a rough idea of the total rated rads output and the actual/estimated dT.

Does that pump display only the RPM in that box?, ie some can display the calculated flowrate if selected.
(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM

Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Return 58

I will check the pump re the calculates flow
 
OK here are my numbers.
Why is the boiler temp so low at 48C (SP 65C) assuming a heat demand of "only" 19.88kw for the kitchen manifold??.
You can see why the Blr pump speed is far greater on the kitchen manifold vis the Laundry manifold due to the different flowrates required, 21.92LPM vis 4.71LPM respectively.

The very low pump speed on rads only at 891LPM for a flowrate of 19.23LPM is indeed puzzling, would have expected it somewhere up to 1700/1800 RPM based on the blr circ pump speed of 1870 RPM required for the kitchen manifold with its blr circ pump flowrate of 21.92LPM.




(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM
Blr circ pump flowrate, 21.92LPM (Manifold output, 19.88kw) Pump RPM 1870.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.


Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Blr circ pump flowrate, 19.23LPM (Rads output, 16.10kw, based on mean rad temperatures)
Pump RPM 891





Return 58
 
OK here are my numbers.
Why is the boiler temp so low at 48C (SP 65C) assuming a heat demand of "only" 19.88kw for the kitchen manifold??.
You can see why the Blr pump speed is far greater on the kitchen manifold vis the Laundry manifold due to the different flowrates required, 21.92LPM vis 4.71LPM respectively.

The very low pump speed on rads only at 891LPM for a flowrate of 19.23LPM is indeed puzzling, would have expected it somewhere up to 1700/1800 RPM based on the blr circ pump speed of 1870 RPM required for the kitchen manifold with its blr circ pump flowrate of 21.92LPM.




(BOILER FLOW TEMP SET TO 65)

Kitchen ufh manifold (troubled)
Boiler/manifold flow temp 48 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 28.5 LPM
Blr circ pump flowrate, 21.92LPM (Manifold output, 19.88kw) Pump RPM 1870.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.


Total Radiator output 19kw
DT across Rads 12 degrees
Flow 70
Blr circ pump flowrate, 19.23LPM (Rads output, 16.10kw, based on mean rad temperatures)
Pump RPM 891





Return 58
The boiler will not get any higher than 48 degrees with heat only on kitchen manifold, I have again just now watched it SP is 65, flow no higher than 48 and boiler has been running for 48 mins continuously. I am totally stumped as to why the boiler does not perform when heating kitchen manifold.
 
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
 
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
It’s derated to 26kw.
The only logical explanation is that the demand is > than the boiler output?. I think you said somewhere that the boiler is actually derated to 23kw so not far away from the nearly 20kw kitchen demand, you might consider reduving the TMV setpoint to 38/40C, this should result in a reduction in the heat emitted by the loops and allow the boiler to get up to its SP temperature.

I will look up the boiler output nozzle rating and see what output it gives at 14.0bar.
It’s derated to 26kw, using a danfoss .55 80s, air setting 3.5.

I understand the different LPM kitchen vs Laundry but the kitchen flow is 5m from boiler and the laundry flow is 31m from the boiler, I thought the distance would also play a role in the laundry manifold flows.

Pump does not give me any flow rates.
 
Pipe (friction) losses are proportional to the square of the flow, so the losses at a flowrate of 4.71LPM are tiny with the piping sizes you have ~ only 5 to 6% of the losses at 20LPM. Your rads have no problem with a circulation demand of 19.23LPM.
 
Pipe (friction) losses are proportional to the square of the flow, so the losses at a flowrate of 4.71LPM are tiny with the piping sizes you have ~ only 5 to 6% of the losses at 20LPM. Your rads have no problem with a circulation demand of 19.23LPM.
I thought that was the case. Does the kitchen manifold need a bypass on it?

Just done laundry manifold, boiler temp SP 60c, flow out of boiler 71.6 degrees, return to boiler 43.1. Boiler stopped firing for 2 mins flow was still 62 degrees when boiler refires, return 44
 

Attachments

  • image.jpg
    image.jpg
    379.1 KB · Views: 36
Last edited:
Why does the kitchen manifold require a bypass??

What was the laundry manifold (mixed) temp? and was the manifold flowrate still 28.5LPM?.
If the boiler/manifold return was 43/44C then the manifold temperature had to be 6C to 8C higher so TMV not going much at a SP of 40C??

NOTE: Its the kitchen manifold SP temp that I suggested reducing to 38C/40C?? to see can the boiler increase to its cut out temp. Forget the laundry, it seems to be OK.
 
Last edited:
Why does the kitchen manifold require a bypass??

What was the laundry manifold (mixed) temp? and was the manifold flowrate still 28.5LPM?.
If the boiler/manifold return was 43/44C then the manifold temperature had to be 6C to 8C higher so TMV not going much at a SP of 40C??
I remember the plumber telling me if the pumpset was changed a bypass would need to be fitted, I'm not sure why :))

We have no bypass on our system at all.

Laundry manifold mix temp was flow 45 return 35, boiler return 44. I am picking a lot of water returning back to the boiler through the stupid pumpset on laundry manifold.

Another question I've been thinking about today, Our expansion vessel connects into the firebox (I think that's what its called) of the boiler, I am wonder when they removed the internal pump this vessel was removed from flow pipe. I'm not sure on this just asking out of curiosity. Where actually is an expansion vessel suppose to be connected to? Thanks john you are very helpful.

You can see in the 2nd image an updated model boiler than ours and the expansion vessel connects into the flow pipe.
IMG_9383.jpg
Screen Shot 2022-07-22 at 7.28.09 PM.png
 
Must go out for a hour or so, will revert later, can you run that test on the kitchen manifold.

The Laundry manifold TMV is performing perfectly as you can see by your findings, below, with mixed flowtemp of 45C (boiler at 70C) , there is not a lot of water returning to the boiler, only 4.,71LPM?.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
 
Must go out for a hour or so, will revert later, can you run that test on the kitchen manifold.

The Laundry manifold TMV is performing perfectly as you can see by your findings, below, with mixed flowtemp of 45C (boiler at 70C) , there is not a lot of water returning to the boiler, only 4.,71LPM?.

Laundry manifold
Boiler/manifold flow temp 70 c
Manifold mixed flow temp 45
Manifold return temp 35
Total flow 16.5 LPM
Blr circ pump flowrate, 4.71LPM (Manifold output, 11.50kw,) Pump RPM 1080.
if only our kitchen one would perform nicely, yes will run that test now.
 
if only our kitchen one would perform nicely, yes will run that test now.
Ok so here goes

Boiler setpoint = 65 c
Pump RPM 1350


Boiler flow and return - Boiler fired continuously for 61 mins,
F = 48.8 - R = 32 after 5 mins
F = 53.6 - R = 34.7 after 15 mins
F = 55.6 - R = 36.6 after 30 mins
F = 56.2 - R = 37.3 after 40 mins
F = 56.6 - R = 37.5 after 45 mins
F = 56.7 - R = 37.5 after 50 mins
F = 56.8 - R = 37.6 after 55 mins
F = 56.8 - R = 37.6 after 60 mins
FINAL FLOW = 56.8 C RETURN 37.6 C

Manifold TMV = 40 c
Flow and return
F = 45.0 - R = 34 after 6 mins
F = 47.2 - R = 35 after 16 mins
F = 48.6 - R = 37 after 31 mins
F = 48.6 - R = 37 after 46 mins
F = 48.6 - R = 37 after 51 mins
F = 48.6 - R = 37 after 56 mins
F = 48.6 - R = 37 after 61 mins
FINAL FLOW = 48.6 C RETURN 37

Boiler/Manifold Flow temp 56.8 - setpoint 65 c
Manifold Mixed temp 48.6
Manifold return temp 37
Total flow 27 LPM

Interesting that the radiators and Laundry manifold get 10 degrees above boiler set point but kitchen manifold never reaches boiler set point.
 
Last edited:
The above gives a manifold demand of 21.85kw so the boiler output must be there or there or there abouts the same since it can't reach its SP and cut out, I suppose the manifold temp of 48.6C isn't bad control since we don't know how accurate the TMV SP index is, you might reduce it to 30C sometime to see reduced manifold output and boiler cut out

For interest, you can see the bypass flow required to increase the boiler return temp from 37C to 45C.

The position of the EV connection is effectively into the pump suction in your boiler and it the new original seems to be into the pump discharge with the pump pumping into the return, probably OK in both cases.

Boiler return 37C (no bypass)
1658486047559.png



Boiler return 45C (with bypass)
1658485935181.png
 
The above gives a manifold demand of 21.85kw so the boiler output must be there or there or there abouts the same since it can't reach its SP and cut out, I suppose the manifold temp of 48.6C isn't bad control since we don't know how accurate the TMV SP index is, you might reduce it to 30C sometime to see reduced manifold output and boiler cut out

For interest, you can see the bypass flow required to increase the boiler return temp from 37C to 45C.

The position of the EV connection is effectively into the pump suction in your boiler and it the new original seems to be into the pump discharge with the pump pumping into the return, probably OK in both cases.

Boiler return 37C (no bypass)
View attachment 76763


Boiler return 45C (with bypass)
View attachment 76762
So should we put a bypass in somewhere? there was one on the side of the boiler teed into the flow and returning back into the bottom of the boiler ? The nozzles they have had in this boiler are 0.55 80 s 2.11kg/h and a .50 80s 1.87 kg/h. Thank you for your spreadsheets they are very informative.

Another question, sitting here reading the installation manual, with the nozzle currently in the burner, it refers to blast tube T3 to be installed, we currently have a T5 installed, would this cause an issue?
 

Attachments

  • IMG_9428.jpg
    IMG_9428.jpg
    262.1 KB · Views: 45
  • tempImagefdGIQH.png
    tempImagefdGIQH.png
    4.3 MB · Views: 36
  • tempImagezEDnFY.png
    tempImagezEDnFY.png
    3.5 MB · Views: 41
  • tempImagetft89x.png
    tempImagetft89x.png
    3.9 MB · Views: 36
Last edited:
I wouldn't have it as my top priority just now but can think about best way to achieve it, would be inclined to try a "Tapstat" with the sensor on the boiler return set to 45C (or whatever min return temp required).

How long is it taking the UFH to get the room (kitchen?) temp up their desired temp, at the moment the room/ambient dT isn't particularly bad, so roomstat should be cycling fairly often?, and the rooms with rads??.
Do you intend to increase the boiler output??.

The installed blast tube should be as recommended, I have a feeling that the reason for the small nozzle with the extremely high pump pressure is to get the emissions right, a, say, 0.65 nozzle with a more modest pump pressure of 10bar + the T3 should give the same boiler output and probably less flame impingment on the baffles.
 
Last edited:
I wouldn't have it as my top priority just now but can think about best way to achieve it, would be inclined to try a "Tapstat" with the sensor on the boiler return set to 45C (or whatever min return temp required).

How long is it taking the UFH to get the room (kitchen?) temp up their desired temp, at the moment the room/ambient dT isn't particularly bad, so roomstat should be cycling fairly often?, and the rooms with rads??.
Do you intend to increase the boiler output??.

The installed blast tube should be as recommended, I have a feeling that the reason for the small nozzle with the extremely high pump pressure is to get the emissions right, a, say, 0.65 nozzle with a more modest pump pressure of 10bar + the T3 should give the same boiler output and probably less flame impingment on the baffles.
Its taking 1 hour to get the floor temp up 3 degrees differential in the kitchen and it has a cycle time of approx 3 hours.

Yes I intend to increase the boiler output, but I'm unsure whether 35kw is enough output for UFH, & Rads. I will also get blast tube changed to instruction manual specs.
 
Its taking 1 hour to get the floor temp up 3 degrees differential in the kitchen and it has a cycle time of approx 3 hours.

Yes I intend to increase the boiler output, but I'm unsure whether 35kw is enough output for UFH, & Rads. I will also get blast tube changed to instruction manual specs.
If we have
21.85kw ufh kitchen
11.50kw ufh Laundry
16,50 Kw Radiators/Trench
3 Kw DHW
A total of 49Kw a 35 kw boiler is not going to perform very well is it if they all demanded heat at once.?
 
Yes, but there are lots of ways of skinning a cat, if the kitchen has a cycle time of 3hrs, 1 hr on time so kitchen average requirement is 21.85x0.33=8.3kw, ideally the UFH should give this output continuously and the manifold output can be reduced by various means, reducing the mixing temperature for example so assuming Laundry similar at 11.5x0.33=3.8kw, then continuous UFH demand is ~ 12.1kw, the rads might cycle in a similar fashion, so you may well find that 35kw output is quite sufficient.? You measured your oil consumption at ~ 23LPD or ~ 10kwh/hr so not a mile away from the above?.
 

Similar plumbing topics

C
Seems reasonable but I'd still rather have...
Replies
1
Views
888
Hi, thanks for the reply, that did cross my...
Replies
2
Views
887
Off the sound of it I would say 15/50. Not...
Replies
1
Views
915
Have to do it someday and it make sense for...
Replies
22
Views
3K
You will need a check valve to stop reverse...
2 3
Replies
61
Views
7K
Back
Top