It’s a shame the kitchen manifold doesn’t run like this. I ran it after this manifold and could not even get the flow temp out of boiler up to 55, but yet this got to 76.5 at boiler
Another thing I noticed today, if you reduce the pressure on the pump while radiators are calling for heat the flow temp rises and so does the return temp.
But if you reduce the pump pressure when the UFH is calling the flow temp rises and the return temp drops.
Yes I can’t work out why the flow temp at 1 isn’t the same as the boiler. Output of 4.1kw.Yes, it's working as I thought it might, apart from temp 1 at 60C which should be the same as the boiler flow at 76.5C or vica versa. The TMV is controlling (first mixing) the temp at 48C = temp 5, this is then (second) mixing with the manifold return of 34C to give a final mixed manifold temperature of 38C, there is only a dT of 4C across the loops so do your calc, LPM*60*dT/860, to give the loop output, kw.
The TMV mixed flow temp of 48C is returning to the boiler which is very good from a balanced corrosion and efficiency point of view, obviously if you require the manifold flow temp of 38c increased then you have to increase the TMV setting.
Its quite a clever control system IMO especially for a oil fired system as it obviates the need for recirculation if the manifold return was returned to the boiler.
It’s a shame the kitchen manifold doesn’t run like this. I ran it after this manifold and could not even get the flow temp out of boiler up to 55, but yet this got to 76.5 at boiler
Another thing I noticed today, if you reduce the pressure on the pump while radiators are calling for heat the flow temp rises and so does the return temp.
But if you reduce the pump pressure when the UFH is calling the flow temp rises and the return temp drops.