Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss How close can a boiler flue be to a window? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
C

cascas

Hi,

I am currently planning a kitchen lay out, which may involve replacing a combi boiler to a position next to a window. How close to a window can a flue be installed? If the window is constructed so only one side is opening, is this distance measured to the opening in the building (i.e fixed window), or the actual window opening? Make/Model of boiler is not determined yet, so cannot check MI instructions
 
Last edited by a moderator:
Usually 300mm if fan flued. This is from edge of flue to the rubber window seal.

Ie if the window is non openable at the flue end then it's ok but if the openable windows seal Is closer than 300mm then it's not ok.

This is for fan flued only, some balanced flue are 600mm dependant on chb kw size. Read the instructions, the distances can all be different
 
check manufactures intructions as that is the overiding factual document
 
Usually 300mm if fan flued. This is from edge of flue to the rubber window seal.

Ie if the window is non openable at the flue end then it's ok but if the openable windows seal Is closer than 300mm then it's not ok.

This is for fan flued only, some balanced flue are 600mm dependant on chb kw size. Read the instructions, the distances can all be different

Im pretty sure its from the center of the flue to the start of the opening i know not much difference and a little padantic but can sometimes make a difference that 35mm
 
Im pretty sure its from the center of the flue to the start of the opening i know not much difference and a little padantic but can sometimes make a difference that 35mm

A building opening could be an unopenable window. A flue fitted close to this would be ok as their is no potential for danger as the window cannot open.

It's defo the window seal and edge of flue
 
As far as I'm aware, the Building Regulations take precedence. Manufacturers instructions generally just repeat what's in the regs and can't in any case be less stringent. Take a look approved document 'J' page 49:

Planning Portal - Part J (Heat producing appliances)

This is what your council building inspector will assess the installation against.
 
Im pretty sure its from the center of the flue to the start of the opening i know not much difference and a little padantic but can sometimes make a difference that 35mm
I'd say you measure it from the outside of the flue. It might be pedantic, but try to explain it to the Gas Safe.
 
I'd say you measure it from the outside of the flue. It might be pedantic, but try to explain it to the Gas Safe.

This is correct.
The manufactures instruction will tell you what you need to know.
 
yes you measure from the outside of the flue not the center/poc tube. if you use a plumage kit then it may be possible to fit the flue at 150mm away from the opening following manufactures instructions of course.

building regs requires that nothing is fitted within 150mm of the building opening meaning brickwork not window to ensure the structures strength is not compromised.
 
AW is correct, it is 300mm from an openable window, but if it is to be not openable you can reduce to 150mm. 150mm is the closet you can be this is building regs not gas regs. Again it is to the outside not the centre of the flue, so you must measure to the closest part. You could go to 150mm to an openable window if you want to fit a pluming kit.
 
i am fairly comfortable that the boiler will be a fan flued RS boiler so once confirmed then the flue at its nearest point needs to be at least 300mm away horizontally from any opening in the building, however the other dimension that seems to escape "hundreds" of re-assessment guys when they come to us is that any part of the flue must be at least 150mm horizontally from any opening in the FABRIC of the (with the fabric opening being where the window frame meets the brick) so it isnt simply a case of saying it can be near the windo as the opening is the other side of the window if that means it contravenes the 150mm rule at the dead light side
 
Im pretty sure its from the center of the flue to the start of the opening i know not much difference and a little padantic but can sometimes make a difference that 35mm

c'mon ryan think about it, it can NEVER be the centre of a flue it must always be the nearest point, eg you have a 100mm flue and measure from the centre, then go to another house that has a 150mm flue and again if you measure from the centre there is more flue within range of the window, however if you measure every flue from its nearest point then the diameter of the flue is irrelevant and therefore the volume of POC's getting to the window will always be the same
 
AW is correct, it is 300mm from an openable window, but if it is to be not openable you can reduce to 150mm. 150mm is the closet you can be this is building regs not gas regs. Again it is to the outside not the centre of the flue, so you must measure to the closest part. You could go to 150mm to an openable window if you want to fit a pluming kit.

i think there was a TB about this saying that you cannot fit a plume kit to try too legitimise an otherwise illegal flue, ie one within 300mm of the opening, as a plume kit is to divert legal POC's away to stop it being a nuicance, although we have a mantra of MI overrule everything, this is where the building regs need to be looked at in conjunction with the MI as it isnt enough to say the flue is fitted as per MI (ie 300mm from next doors window) IF next door say it is causing them distress, unless you mean using a plume kit to raise the terminal up and therefore cancel out the 300mm requirement as the terminal is now above the window
 
But doesnt every M.I state that it is 300mm from an opening window, Door etc.
I may be wrong but I am sure none of them say window they say opening window.
 
Last edited:
yes many manufactures will allow you to use the plume kit to raise flue away/above window and this allows you to have the flue/air intake at 150mm from opening.
 
I have on many occasions. I had one 2 weeks ago, had only one place for the boiler, upstairs A/C, had to put flue out horizontal which was close to a window opening onto it as it was a huge 1 pane window that opened right out. SO I fitted a pluming kit and all was fine, no probs with clearances and no danger of POC getting in as I ran it 1m away.
 
Don't know about you lot, but plume kit or not, I wouldn't sleep easily knowing there's a flue 150mm from my window. Or 300 if I'm honest. Yes we all have occasions when things are tight, and you have to fit within your legal limits. However I always try and make the distances between flue terminals and openings as big as possible. For my piece of mind.

I looked at a boiler late last year that conformed to all legal clearances. However due to the location of the window (about 350mm from flue terminal) and the front door, a wind tunnel effect was happening. Pulling POC's into the property.

I was called to repair the boiler, and complete a CP12. I advised the landlord to permanently seal off the window, which he did. Only then was I happy to sign it off. Despite the fact that another engineer who is more cavalier would have signed it off as it was.

In short, yes conform to the legal clearances, but also use your loaf, and ask yourself, would I go to sleep in that room, with that flue so close to the window? Would I let my children sleep in that room? If the answer is no. Then don't do it. Most people will be grateful for your integrity.
 
But doesnt every M.I state that it is 300mm from an opening window, Door etc.
I may be wrong but I am sure none of them say window they say opening window.

generally the MI will say 300mm from ay opening in a building eg a window or a door, but remember that also means the wee plastic slot vents you get between the vertical joints in bricks on facing brick walls, and also remember it tells you to comply with BS5440-1, which is where the 150mm to the fabric opening is found
 
But the regulations are here to help us, A Corgi Inspector told me that if the flue was letting POC into the window it must therefore be open, then it will then be drawing in more than enough fresh air in to cancel the fumes. Makes sense I suppose.
Why would you not trust a pluming kit?? You can then take it metres away if you want.
 
But they also say you can fit a pluming kit if you are less than the 300mm so who is correct?
I have fitted many and surveyed many on numerous contacts when less than 300mm from door or openable window and never had any trouble, all inspectors advise this rather than moving boiler position.
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

P
    • Like
As above through the roof. Also I doubt that...
Replies
2
Views
3K
I beg to differ on that. The exhaust is the...
Replies
7
Views
2K
  • Question
Exactly it's our opinions but that opinion...
Replies
22
Views
3K
E
It sounds like that needs to be sealed from...
Replies
3
Views
1K
If it were me I would send a letter recorded...
2 3 4 5 6 7
Replies
154
Views
40K
Back
Top