Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Choosing the right boiler - somewhere between 18kw and 42kw depending on where I look..... in the Boilers area at Plumbers Forums

Status
Not open for further replies.
They do a system version I believe;

Greenstar i System (27kW and 30kW) | Worcester, Bosch Group



Perhaps not quite finger in the wind, it seems a fairly detailed estimate using this calculator;

Calculate heat requirements


I would recommend you get a Heating Engineer to look at it. Either to price you for the work or to give a report and Heat loss calculations.
They will probably charge for the latter but it would be worth it in my opinion.
I just took a quick look at the calculator you used and it did not give the answers I expected to see.
 
I would recommend you get a Heating Engineer to look at it. Either to price you for the work or to give a report and Heat loss calculations.
They will probably charge for the latter but it would be worth it in my opinion.
I just took a quick look at the calculator you used and it did not give the answers I expected to see.

Do my numbers look on the low side? The boiler sticks out 30kw CH against my estimation of 19kw, so I figure that even if I'm out by a huge margin then I'm still on the safe side. And when I did my calcs I was pessimistic about certain things (e.g. wall insulation - fairly sure they're all cavity insulated by chose non-insulated in the calculator).

That said, I will do as you suggest and get in the pro's......

As a matter of interest, what tool do the pros use?
 
Do my numbers look on the low side? The boiler sticks out 30kw CH against my estimation of 19kw, so I figure that even if I'm out by a huge margin then I'm still on the safe side. And when I did my calcs I was pessimistic about certain things (e.g. wall insulation - fairly sure they're all cavity insulated by chose non-insulated in the calculator).

That said, I will do as you suggest and get in the pro's....

As a matter of interest, what tool do the pros use?

Personally I use a Mear Calculator, as well as knowledge and experience.
I have looked at a few online tools/calculators but I can't trust them the same.
I would size the Boiler for whichever has the largest requirement, DHW or CH, in your case.
Others will look at that different.
 
Mears all the way unless I just need a quick advisory calc
 
Evening all,

Our boiler hasn't been doing very well recently. Just doesn't get the radiators hot at all. It was a relic of a smaller house, which was then extended. They didn't replace the boiler.

We've decided to replace the boiler and sort out some pipework, install new valves etc, but I can't settle on the boiler size required. All radiators are already installed etc, so it's a question of finding the right sized boiler to heat it all appropriately;

- 4 bed detached house
- 1 bath, 2 showers
- 2200 sq/ft
- 15 rads, 2 towel rails

We are going for a system boiler. My calculations are as follows

- Current radiator output (Watts - ΔT = 50°) = 22620 Watts (includes towel rails and two rads in a glass conservatory)

- House heat loss = 19000 Watts (17000 if remove conservatory)

The boiler which has been suggested is the Worcester-Bosch Greenstar 30i. As far as I can tell it has 24kW CH output, and 11ish LPM flow, with a max BTU of 100,000.

If I trawl the internet I find all sorts of stuff about 3kw per radiator, or any 4 bed houses needing 42kW boilers etc. I appreciate that in the past it's been common to massively oversize boilers, but it just makes me nervous that I'm missing a trick and the boiler won't be capable. With the numbers above would the 30i suffice and are there any apparent issues? I have the numbers but don't really know how to interpret them...

My alternative is to have the 35CDI or something, at a marginally greater cost.

Many many thanks.

Well done on your maths work mate. TBH you’ve done a better job than most plumbers. Speaking from experience you should be fine with Worcester 30i system boiler, or Worcester 30 CDI is Avery good boiler for a bit more money.
If you wanted full peace of mind you could upgrade to the 35kw boiler, but yo give some idea I’m maybe looking at the 35CDI to heat a block of four flats whilst providing all the hot water too. Dan :)
 
I would say that's for a standard copper cylinder not an unvented, As if you allow let's say 2kw

And the unvented cylinder can do a reheat time of 30 mins with 20kw, that will give you a re heat time of 5 hours from cold

So if you use all your hot water it will take 5 hours for it to be fully hot[/QUOTE

I know its different as electricity but Even an immersion heater say 2kw of electric power would heat the tank in short period
 
Status
Not open for further replies.

Similar plumbing topics

P
Baxi boilers are light and quiet but I doubt...
Replies
15
Views
2K
R
    • Like
  • Locked
Sorry but I don't have time to read the...
2 3 4 5
Replies
110
Views
21K
T
  • Locked
Assured Heating - do the Worcesters come with...
Replies
14
Views
2K
Truman
T
C
  • Locked
Thanks to all for your help :):):) This is...
Replies
8
Views
2K
C
M
  • Locked
Seems to me that if you're questioning the...
Replies
7
Views
3K
Back
Top