Discuss Grundfos Alpha 3 Pump Settings for Hydronic Balancing in the Plumbing Jobs | The Job-board area at Plumbers Forums
Ok, you beat me to it...
Trying to get the acronyms
Is that;
Turn on Hot Water only, to open coil, set pump to constant Pressure with set point 3m?
Ok, you beat me to it...
Trying to get the acronyms
Is that;
Turn on Hot Water only, to open coil, set pump to constant Pressure with set point 3m?
I’ve just noticed that the Smart TRV app is showing an error, might mean that one of the TRV maybe malfunctioning... can’t tell from the app would need to remove all the Smart TRVs to ensure it’s not causing an issue...
- That would have to wait till tomorrow to test as the wife is sleeping.
It didn’t have an error earlier on during our tests...
I’ve just noticed that the Smart TRV app is showing an error, might mean that one of the TRV maybe malfunctioning... can’t tell from the app would need to remove all the Smart TRVs to ensure it’s not causing an issue...
- That would have to wait till tomorrow to test as the wife is sleeping.
It didn’t have an error earlier on during our tests...
I have now gone around and opened up all lockshields fully, taken off all TRVs, I have switched on the CH and HW.
The bypass is set as described previously.
Here are the status reports from the app:
- The Max Estimated Flow rate has increased to 0.9 m3/h
- When the heating or HW circuit is closed the max drops to 0.8 m3/h
CC Max
View attachment 36997
PP Max
View attachment 36998
CP Max
View attachment 36999
CP 3M
View attachment 37000
PP 3M
View attachment 37001
Auto Adapt
View attachment 37002
Hi John,
many thanks for your detailed post in return.
I had overdone things yesterday and the day before, playing with the heating system, as a consequence I wasn't able to sum up the strength to reply to you last night, so my apologies.
I saw from your profile that you lived in Cork, hence I realised that asking you to come and look at my heating might be a bit problematic )
- I once went to a wedding in Cork, lovely place to visit... Spent the whole wedding night woohing some lass from America, early hours down by the harbour, getting locked out of my digs, somehow ended up in 'her' room.. now that holds good memories
You have an interesting background, mine is 30 years in software development/engineering/design/etc both as an employee and running my own one man band. Interestingly, I did 5 years contract work at GSK. Right now, I'm an employee for an Investment Bank, however due to long term Illness/disability I'm unable to work.
So, though i'm not a plumber in any shape or form, I have a fairly good understanding of how things work and a high capacity to learn quickly, smartly and most importantly correctly.
- What I find challenging, like in most technical industries (IT is the worst), is that accurate/useful information is hard to get, many people who are experts, understand day to day practical things but don't have the capacity/ability to share their knowledge to educate others, with many hiding behind the 'oh you will not be able to understand mantra', when it is in fact they just don't have the knowledge themselves.
- Technical support helplines are a hit and miss affair, Grundfos is a typical prime example of a particularly bad one, when I've called them for advice on their own products they hide behind the 'unless you are a G3 Engineer/system designer' we aren't talking to you... or we don't give advice you will have to talk to your system designer...
Then even when I've escalated to their Head of Customer Support and clearly demonstrated my capabilities and that their software product has no documentation, is full of holes/bugs and is totally unusable... Their claim is it doesn't need documentation as any G3 Engineer can use it... Interesting that their product refers to terminology that doesn't appear anywhere on the entire internet...
- I may later, if you are willing, ask you some questions that may point some light on questions I have about this software...
Anyway, sorry to babble on, but it's always interesting to have a side conversation going on..
The noise comes about when throttling down the lockshields to restrict flow and then upping the pressure output of the pump to get enough flow around the system...
- I need to try running the pump in PP Max mode after balancing, to see if it solves the noise issue, I was using constant curve.
With all the lockshields fully open, the noise disappears, however as a consequence, some of the Rads, mainly the ones in the downstairs front room don't heat.
FYI, going back to the original reason for wanting to balance the system was:
1) Front Room, Bedroom 2, Ensuite Shower Room not able to heat up and maintain heat when outside temperature <5c.
- Doesn't help that New Build House has insulation issues. This is being worked on, but a major problem getting builder/warranty company to fix, but slowly getting there... (Working on this for 3yrs!)
2) Rads overheats easily.
3) TADO smart TRVs struggles with the issues above.
4) Boiler continuously short cycles.
Software Balancing
------------------
I would like to retry using the Grundfos 'Go Balance' software:
Theoretically, it should work well, it uses the pump's abilities to measure flow/pressure/etc to detect the heating system and radiator capabilities, together with user input to calculate heat loss... It will then guide the user to throttle each radiator to set a certain flow.
- However, when I've used this software, some inputs i've had to guess, which could be the reason that it hasn't worked well... - Some rads not heating well, always at least one cold... (The software gives a choice of running system in AutoAdapt or PP afterwards, I had always gone with AutoAdapt, which may have not helped..)
If you are, willing, I would like to run the user inputs past you, as you probably can come up with far better inputs to use... Let me know if it is ok to ask?
Manual Balancing
----------------
If in the end the software fails to get it right, I will then need to use manual balancing with a temperature gauge (I have an InfraRed Flur gun) - I did struggle to know what mode to run the pump in, to mimic Fix Run Speed 2, but I'm thinking CC set to a setpoint of 65%??
AAV
---
Yep, learnt my lesson previously on this one, I have the AAV closed after removing air from the filling process.
- It would be hard to fit a isolation valve, purely due to the AAV currently screwed into a bolt that has been solder into a Tee that itself is soldered into small very tight pipework, redoing the pipework would take major surgery and the other issue is I haven't taught myself how to solder (yet), so ideally I would be using compression components, which isn't ideal...
I haven't closed the Air Separator, should I?
ABV
---
I'm not actually sure if one is actually needed... It have never seen it open in AutoAdpat/PP modes and I have not had any issues with my boiler when the heating circuits and bypass are closed, even though the boiler manual states a bypass is required.
- Interestingly though, Glowworm support have told me that the boiler has no minimum flow requirements, which contridicts the manual.
Delta T through the Rads.
------------------------
Part of the exercise to gather information for the 'Go Balance' software, I have all the technical specs of each radiator and specifications of each room, plus me Infrared temperature gun.
Magnaclean
----------
I fitted it in December, checked in on Thursday, it was practically clean, a miniscule amount on it.
- Interestingly, when I put the ABV back on Thursday, the elbow I took off (which was put in its place when I took it out, had a bit of blackness settled in it. Guessing it had settled there due to the manual bypass being closed)
Pipework Layout
---------------
As far as I can tell the pump is on the flow side, certainly the flow pipe from the boiler heats first, the pump is before the 2 way valves to radiator/HW circuits.
I can't be 100% sure as pipework is hidden between boiler and airing cupboard that contains the pump, valves, expansion tank, HW cylinder.
Is there a sure way to tell??
Expansion Vessel position
-------------------------
The pipework to the expansion vessel comes off the return pipework back to the boiler.
I've attached a photo of the pipework, let me know if more photos are required.
View attachment 37026
Legend:
A - Return to boiler.
B - Flow from boiler.
C - Radiator return from downstairs and upstairs rads.
D - Flow to downstairs radiators.
E - Cold Water feed.
F - Hot water out of the cylinder.
Note:
The 2 way valves for downstairs and upstairs are wired together, I did this as TADO only works with one physical zone. - I may at a later date, re-pipe to only have one 2 way valve to control the radiator circuit.
The layout of return pipework from the radiators, HW cylinder and the bypass has always put a question mark in my head, as it doesn't look right, however, I don't know what a correct layout would look like... What do you think?
Right, I will stop for now, I think there is a mass of information for you to read and a ton of questions, I again thank you for helping me out, I hope this is all interesting for you.
Cheers!
Richard.
Ps, If you ever want to chat on the phone or switch to email, let me know.
Pps, I might struggle with the accent
Thanks, John, for the reply, it's interesting every time to see what your thoughts are...
I presume to check that the pump is on the flow side of the boiler is by feeling where the heat goes...
Whenever I've checked, the first pipe to give off heat is the one below the pump, which should be correct one as the arrow on pump is pointing upwards and the arrows on the two-way valves are pointing away from the pump...
Getting rid of air is a questionable one as I can't find any air anywhere but always have a suspicion that air is trapped somewhere.
- One interesting thing I have seen time to time with the new gauge below the expansion tank is that, when I let the system cool down I see the pressure drop on the gauge, I then top the system back up, it will rise rapidly, going from say 0.5bar to 1.5bar, then I turn the system on to heat for a bit, stop it, let it cool down and then again I see the pressure drop to 0.5bar, then I top up again... I had to repeat this process numerous times on Thursday (after putting the ABV back and changing the TRV bodies) till eventually it stopped occurring... However, yesterday when playing around, a few times I let the system cool down to then find myself with a pressure drop... which I then filled again... repeating a few time... It got me questioning whether the filling loop which is using 10mm flexible braided hose, is too narrow and perhaps is introducing air into the system... Being that the water entering under 3bar of pressure is separating as it is forced through the 10mm hose... I'm sure I've read that this can happening...
When you say about up/down radiators not heating together, I'm not sure if that is the case or maybe I have described it incorrectly...
Both upstairs and downstairs are heating up, just I would describe it as not in balance... That is that the radiators don't have equal heat on flow/return and some struggle to have heat when the pump is on lower settings...
- I thought that is a typical description of unbalanced radiators... Have I misunderstoood?
FYI, here are some numbers I took yesterday when trying to manually balance with the pump on:
- I think the system had been heating around 10/15 mins, I didn't note it down, I can't remember which pump setting I had it on, possibly CC at 65%, I would need to repeat to be 100%.
View attachment 37039
Isolating valves either side of PRV... What valves, there aren't any that I see... I also believe that have isolating valves should not be either side to ensure the PRV isn't accidently isolated... Can you point out to me what you are seeing?
- I was considering putting a service valve below the expansion tank to allow correct testing of the air side of expansion vessel.
When I pressure tested the air side of the expansion vessel, I had to drain down the water to isolate it...
- Altecnic (Caleffi) tech support advised:
Pressure settings: 1.6bar air side & 1.4bar system side.
I asked about the fact that the pressure gauge doesn't go up with heat and got told that was correct behaviour...
I asked to make sure gauge & vessel were the right way up.
I also asked about air in the system.
It looks like at some point, the conversation stopped, I probably got distracted and forgot about it... So if need be I can go back to them to ask further questions...
How do I check the MVs are opening fully?
- They are both definitely opening, % wise, no idea how to check...
- However, I noticed yesterday that the MV to upstairs was buzzing, which in my mind is an indication that it is starting to fail. In the past one of the MVs failed, I think it was the upstairs previously as well... I know the downstairs one was plumped in backwards, which I only noticed, had corrected in Oct 2018.
- If you think it is wise, I can always do as I said previously, which is take out one of the MVs, so only have one MV for the whole house.. Guess it would then rule out a number of potential issues... would require a little change to the pipework...
Ooohhh, I like your idea of isolating each radiator one at a time, to bleed them... Tomorrow, I will do this, record the numbers and we can discuss results...
- I do remember watching a youtube video which someone did this... What they also did was keep the fill loop open and controlled via PRV, they then isolated each radiator, opening the lockshield drain off to flush air that was trapped out... I actually bought a PRV to do this very thing. However, I didn't actually implement this as I hadn't all the connections to implement and then again got distracted... So, if needed, can do this later...
Anyway, now I'm waffling on, so thanks for the advice, I'll come back to you tomorrow.
This is a report that is produced by the balancing softwere after the balancing process is complete, might be some useful information in this?
Expansion Vessel: You say 1.6 bar air side and 1.4 bar water side, the (cold) filling pressure should never be lower than the pre pressure, ideally it should be 0.3 to 0.5 bar higher to give you a little water reserve of 1 to 2 litres which means very infrequent top ups, your pre pressure of 1.6 bar is a little high to do this but I would advise filling to 1.75/1.80 bar when system is cold but no higher as the boiler safety valve lifts at 3.0 bar.
Obviously you have to top up frequently if your are venting rads etc but once finished then if you still have to top up frequently will be indicative of a leak somewhere so when you have the system back to normal keep a eye on this, I would not recommend the fitting of a PRV, sometimes called a auto fill valve as this masks any leakage problems when left open, this is what I was referring to as I thought that you had one fitted to your fill line.
PRV refers to both a Pressure Relief Valve (safety valve) or a Pressure Reducing Valve.
I will attach a little calculation to show the effect of pre and fill pressures on the boiler final pressure.
Re balancing: I would start with all the L.shield valves fully open and then take the DeltaTs on all of them and only throttle in the ones that have the lowest DeltaTs and do it with the pump on PP5.1 setting, maybe that's how you are doing it anyhow, as I said previously once they are all reasonably balanced then you can reduce the pump head as required to give you a greater DeltaT if required. The main thing to avoid is having ALL the L.shield valves throttled as this can cause noisy operation.
You don't really have to do all those individual tests that I suggested above but it would certainly be interesting.
Just thinking again about any other restrictions in your system, I know that you can't test it but is there any possibility that the boiler heat exchanger is partially blocked? the E.vessel is piped in before this, it will affect pump operation if the exchanger is partially blocked, I don't have any experience of sealed heating systems but I might have thought that the E.vessel piping would have connected in just before the pump suction, but again no problem where it is if the exchanger is clean.
Any link to your Air Separator?.
Very interesting , I must read it properly later on, is that done with just any one rad on at the time?.
I also read that your boiler has a stainless heat exchanger so that's probably why they claim no bypass required.
Hi John,
What do you mean by pre-pressure?
From what I understand, are you saying the complete opposite to what Altecnic support line has advised me?
I.E The water side should be 0.3 - 0.5 than the air side?
Why on earth would they tell me the complete opposite?
- Someone on here prior to that, told me to drop the pressure to 1bar on both sides, when that caused problems, I spoke to Altecnic.
- FYI, I have an 18ltr Reflex expansion vessel fitted.
- I understand about the safety valve set at 3bar.
- I also know/understand not to have the Pressure Reducing valve permanently connected, it was for the purposes of driving trapped air out.
- Do you have that calculation to show the effect of pre and fill pressures on boiler final pressure?
Thanks for the advice on the throttling, i'll probably test/record everything, it's useful info.
I would say a good chance that the boiler exchange is partially blocked, as when I flushed all the Rads, it appeared to me that the system never had inhibitor in it.
The boiler was probably never flushed, it took 2 years for the builder (Persimmons) to send someone in to commision the biler and fill in the paperwork... what with that and black water and small metal fillings that came out when I flushed the rads...
Air Separator
-------------
Spirotech Spirovent RV2 Air Separator (Brass) - -: SpiroVent Air Separator 22mm
Spirotech | maximising performance
View attachment 37045
Thanks, looks like I’ve got my hands full tomorrow...
If I’m going to do the expansion vessel pre-Pressure, I might as well add a service valve:
https://www.NoLinkingToThis/p/tesla...T5Z70ngv-_vkydQXFlhoCc34QAvD_BwE&gclsrc=aw.ds
And whilst I’m doing that, seeing I would drain down the system, what do you think about moving the expansion vessel to the pipework before the pump?
- just in case a partial heat exchange blockage?
- I’ve checked the boiler install instructions put the expansion vessel before the pump and with the pipe layout wouldn’t be to much to move it over...