Grundfos Alpha 3 Pump Settings for Hydronic Balancing | Plumbing Jobs | The Job-board | Page 3 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Grundfos Alpha 3 Pump Settings for Hydronic Balancing in the Plumbing Jobs | The Job-board area at Plumbers Forums

image.jpg
Looks like the service valve has a anti tamper device to stop accidental closure by householder:

TeslaUK launches new Expansion Vessel Service Valve - Installer Online

So guess that allows it to be fitted... They would be in a lot of trouble to launch and sale in U.K. if it wasn’t legal...


Are you sure about moving the vessel, as at the moment it isn’t fitted as advised by Glow-worm..

image.jpg



Thought you prevoislusly said it was better to be before the pump :)

Even more interesting...

image.jpg


Looks like the install doesn’t conform to current regs anyway...
 
View attachment 37046 Looks like the service valve has a anti tamper device to stop accidental closure by householder:

TeslaUK launches new Expansion Vessel Service Valve - Installer Online

So guess that allows it to be fitted... They would be in a lot of trouble to launch and sale in U.K. if it wasn’t legal...


Are you sure about moving the vessel, as at the moment it isn’t fitted as advised by Glow-worm..

View attachment 37046


Thought you prevoislusly said it was better to be before the pump :)

Even more interesting...

View attachment 37047

Looks like the install doesn’t conform to current regs anyway...

I'd say that isolation valve looks ok so its probably legit.

My only concern re moving the E.vessel pipe is that by doing so it may create a low pressure zone before exchanger (if exchanger plugged) and cause air to be drawn further back but if you are happy to relocate it then fine but leave it so as that it can be put back easily in its original location
 
You are like me John, don’t sleep well at night...

Been doing some reading on expansion vessels and pressures...

If I don’t move the vessel, then a different pressure calculation is needed to take into account that vessel is down stream of the pump...

https://www.caleffi.com/sites/default/files/file/01079_en.pdf
- They also do a service valve...

Plus another adjustment is required as the Expansion vessel is on the first floor and boiler is on ground, though 1.5m off the ground.

If you look at the earlier photo of the pipework, it wouldn’t be too difficult as the return and flow pies from the boiler are next to each other (A & B£, so it wouldn’t take too much to shift from the vessel from return to flow...
 
Damn it...

That Caleffi link I sent you states installation of the vessel should be on the return pipe:..

So now conflicting advice...

So stick or twist.. arrggghhh

Another website:

Sizing of expansion vessels

I wouldn,t get too hung up on that sizing, just remember to add the static head from the the E.vessel to the boiler safety valve, in your case ~ 0.25 bar. ( I should have twigged that the boiler wasn't "upstairs").
If I use 2.o litre as your expansion volume (it won't be more with only 8 rads and a gas fired boiler of contents ~ 2 litres) then if you leave the pre pressure as is @ 1.6bar, fill pressure of 2.0 bar you will end up with a reserve of 2.4 litres & a final pressure of 2.4 bar...+ 0.25 bar static head = 2.65bar at the boiler, still OK . If you wish you can drop the pre pressure to 1.0 bar, fill pressure of 1.5bar gives a reserve of 3.3 litres & a final pressure of 2.13bar...+0.25 bar static head = 2.38 at the boiler. Generally the higher the final pressure from a pump point of view the better as long as it doesn't exceed say 2.6/2.8 bar at the boiler.
I have changed several relations E.vessels over the years & all of them were tied in u/stream (before) of the pump, a few of them had the pump on the boiler return (pumping into the boiler) but the E.vessel was still piped in U/stream (before) of the pump.
I have a vented system with a combined vent & cold feed.

The logic is I suppose that if tied in before the pump then the pump suction will be at the E.vessel pressure and the pump discharge will be at the pump head + the E.vessel pressure, if fitted after the pump, the pump discharge will be at the E.vessel pressure but the pump suction will be at the pump head minus the E.vessel pressure.

I would suggest, for the moment at any rate, to leave the E.vessel as is, reduce the pre pressure to 1.0 to 1.2 bar, add 0.5 bar for the fill pressure giving either 1.5 or 1.7 bar fill pressure and see how you go.
When the boiler is then fully heated up with everything on, read off the final pressure and add 0.25 bar to it to give you the pressure at the boiler, you may then decide to up the pressures a little.

Must go for a walk now.

Edit: you said that when you dropped the pre and fill pressure to 1 bar that you had problems.... what kind of problems? ( I asked this already), when both these pressures are the same and if you have a restriction anywhere then the E.vessel & pump suction can fall to zero or near it and create pump problems.
 
Last edited:
Hey, just woke, it’ll be a few hours before I’ll be ready to roll up my sleeves.

I’ve read what you have said above and have decided the plan is:

Shut all off
Empty enough water to remove expansion tank to fit service valve.
Set pre pressure to 1.2 bar.
Fill pressure 1.7 bar.
Remove air as much as possible.
Heat system.
Close all rads and then open up each rad one by one to force trapped air out, taking readings as I go.

One final thought before I start my plan... do I change the fill loop hose & connectors from 10mm to 22mm, to smooth the water flow coming in? Or you think having 10mm will make little difference? Sound wise it sounds like there is a lot of turbulence when adding water...

What you think?
 
Hey, just woke, it’ll be a few hours before I’ll be ready to roll up my sleeves.

I’ve read what you have said above and have decided the plan is:

Shut all off
Empty enough water to remove expansion tank to fit service valve.
Set pre pressure to 1.2 bar.
Fill pressure 1.7 bar.
Remove air as much as possible.
Heat system.
Close all rads and then open up each rad one by one to force trapped air out, taking readings as I go.

One final thought before I start my plan... do I change the fill loop hose & connectors from 10mm to 22mm, to smooth the water flow coming in? Or you think having 10mm will make little difference? Sound wise it sounds like there is a lot of turbulence when adding water...

What you think?

No, I don't think it will make any difference whatsoever, the noise that you are hearing I would think is from the throttling effect across the fill valve in reducing the mains pressure (4 or 5 bar?) down to 1.5 bar or whatever. I hear the same noise when topping up the relations systems.
 
Ok, fair enough, will skip.

What you thoughts of changing the air side pressure without drain down?

I was reading something last night that it might be possible, but the calculations change or is it not a wise thing to do?
- Obviously, skipping a drain down saves me adding more inhibitor.

Let me know your thoughts?

Alternative, would be to pull a vacuum, but i've never done it before. Guessing to risky for a DIYer?
- Just remember, it a pain in the arse to disconnect the expansion tank from the pipework, due to a solid manifold connector, I literally have to dismantle. - Another reason for adding a service valve.

Thoughts?
 
Last edited:
Ok, fair enough, will skip.

What you thoughts of changing the air side pressure without drain down?

I was reading something last night that it might be possible, but the calculations change or is it not a wise thing to do?
- Obviously, skipping a drain down saves me adding more inhibitor.

Let me know your thoughts?

Alternative, would be to pull a vacuum, but i've never done it before. Guessing to risky for a DIYer?
- Just remember, it a pain in the arse to disconnect the expansion tank from the pipework, due to a solid manifold connector, I literally have to dismantle. - Another reason for adding a service valve.

Thoughts?

OK then, I think your happy/sure that the present Pre pressure was/is 1.6 bar.
Fire up the boiler with all systems full open including hot water, turn the cylinder stat fully up to ensure the MV valve doesn't close and ditto with any room stats, when you are happy that the system contents are up to temperature, check and note down the E.vessel pressure and then just open the fill valve carefully and increase the pressure to say 2.0/2.1 bar, this will give you 2.25/2.35 bar at the boiler.
 
Before I do so, is that a safe thing to do in terms of protecting the system & boiler, is running that high ok?
- I presume it is as you are a cautious Guy...

I’m guessing it is fine as it would only be a max 2.3/2.4 at boiler, plus the PRV opens at 3 bar for ultimate protection.
Only question would be is would it be making the boiler work too hard.

Sorry for all the questions.
 
Before I do so, is that a safe thing to do in terms of protecting the system & boiler, is running that high ok?
- I presume it is as you are a cautious Guy...

I’m guessing it is fine as it would only be a max 2.3/2.4 at boiler, plus the PRV opens at 3 bar for ultimate protection.
Only question would be is would it be making the boiler work too hard.

Sorry for all the questions.

No it won't make the boiler work any harder, the main reason for limiting it to 2.25/2.35 bar (E.vessel 2.0/2.1 bar) is to ensure that the safety valve doesn't start "feathering" a little early at say 2.7 bar and continue to leak as they sometimes do especially if a lot of crap has/is circulating around.

Why don't you bring the boiler up to temperature as is and per suggestions above and post the final pressure before going any further? You probably have a fair idea anyway what it is.
 
Doh, there is a setting on your profile blocking PMs, perhaps you are fed up with me :)

The setting to change is under profile -> privacy

Doh, there is a setting on your profile blocking PMs, perhaps you are fed up with me :)

The setting to change is under profile -> privacy
Can someone guide me through this please re changes to make to allow sending private messages or whatever.
 
DF034B27-95A9-463F-96F3-3EBECBFE3C13.png
Can someone guide me through this please re changes to make to allow sending private messages or whatever.

This is how I access it via the mobile app, that icon, 3rd from the left, opens up my profile and then I go to the privacy menu. Scrolling down I get to a setting that lists who can can’t contact me...

Another way to do it, would be to go under my name and press the follow button, you then should be able to send me a PM, to do that press the email icon and type in my username ‘hallra’
 

This just doesn't make sense.

The OP says he has an Ultracom 24 hxi boiler, which has a 24kW output; but the App says the energy consumption is 29kWh. Is that the current rate or the total since the pump was first installed?


FYI, here are some numbers I took yesterday when trying to manually balance with the pump on:
- I think the system had been heating around 10/15 mins, I didn't note it down, I can't remember which pump setting I had it on, possibly CC at 65%, I would need to repeat to be 100%.

View attachment 37039
1. Why are you using a flow temp of 65C? It will reduce the rad output considerably.
2. How, and where, are you measuring the temperatures? The drop of about 20C from boiler to rad seems excessive.
3. The Ultracom is designed for a 20C differential. An 11C differential will result in a pressure loss through the heat exchanger of nearly 6 metres, compared to 1.8m with a 20C differential. This is at max output.

You say, in another post, that the boiler continually short cycles. This is probably due to the boiler being oversized. (24kW for approx 12kW of rads.) The boiler's logic says that, every time it restarts it does so from max output and then modulates down if necessary. Unfortunately it doesn't modulate fast enough so the temperature rises very quickly, the boiler overheats, shuts off, and the whole cycle starts again.

The reason for over-sizing the boiler is: Hot Water. The system "designer" assumes that the HW cylinder is being heated at the same time as the CH is running flat out. The solution is simple - heat the cylinder when CH requirement is minimal or non-existent. (Modern HW cylinders retain their heat for a very long time.) Installations with Weather Compensation have to be configured so that HW takes priority over CH. If it didn't, the flow temperature might not be hot enough to heat the cylinder. Although you don't have weather comp, you could sill adopt the same principle and give HW priority over CH.

It might be possible to reduce the max output of the boiler using parameter d.0 (See the installation manual).
 
This just doesn't make sense.

The OP says he has an Ultracom 24 hxi boiler, which has a 24kW output; but the App says the energy consumption is 29kWh. Is that the current rate or the total since the pump was first installed?



1. Why are you using a flow temp of 65C? It will reduce the rad output considerably.
2. How, and where, are you measuring the temperatures? The drop of about 20C from boiler to rad seems excessive.
3. The Ultracom is designed for a 20C differential. An 11C differential will result in a pressure loss through the heat exchanger of nearly 6 metres, compared to 1.8m with a 20C differential. This is at max output.

You say, in another post, that the boiler continually short cycles. This is probably due to the boiler being oversized. (24kW for approx 12kW of rads.) The boiler's logic says that, every time it restarts it does so from max output and then modulates down if necessary. Unfortunately it doesn't modulate fast enough so the temperature rises very quickly, the boiler overheats, shuts off, and the whole cycle starts again.

The reason for over-sizing the boiler is: Hot Water. The system "designer" assumes that the HW cylinder is being heated at the same time as the CH is running flat out. The solution is simple - heat the cylinder when CH requirement is minimal or non-existent. (Modern HW cylinders retain their heat for a very long time.) Installations with Weather Compensation have to be configured so that HW takes priority over CH. If it didn't, the flow temperature might not be hot enough to heat the cylinder. Although you don't have weather comp, you could sill adopt the same principle and give HW priority over CH.

It might be possible to reduce the max output of the boiler using parameter d.0 (See the installation manual).

Hi Doitmyself (Great username!)

Welcome to the conversation.

Let me by first stating I'm a moderately knowledgeable DIYer, so apologies if I do something incorrect or ask questions that may look to a expert silly.

I will try to answer your questions as best as I can, however, be aware, that I am still gathering information, testing things out, so it is a work in progress, a lot of work/progress has been made behind the scenes. - A BIG thanks to John.G!
- Thus, it is probably wise to park questions for now as many things are changing on a rapid basis and thus I won't be able to keep you up to speed with everything.
- Once the situation has settled and good progress made, I will post an updated status.


Background
----------

The Heating System was designed and installed by the builder 'Persimmons', it has never worked well since day one, they have constantly avoided fixing issues, I've had to make a number of changes due to component failures and/or incorrectly installed components. (Valves the wrong way around, non-commissioned boiler, failed pumps, failed expansion thank, leaks, etc, etc)

- I've had to live in the cold for some time, as in cold spells the system hasn't heated the house well. Which doesn't help me at all, as I have a severe longterm illness/disability, the cold cripples me.


Replying to your comments
-------------------------


The energy consumption is from a status page of the mobile app that talks to the pump via bluetooth, it is not connected to what the boiler is consuming.

1) The boiler is set to 65c as was advised by Glowworm, we are looking at adjusting this.

2) For the temperature readings you refer to, I had a InfraRed Gun pointed at the steel panel of the radiator, about an inch in from the flow and return valves. (Valves are at the bottom of each rad)
- These numbers were taken with the pump settings too low and lockshields closed a fair bit.
- Through testing, pump settings and throttling has changed a fair bit and far better results are being seen, will publish numbers again when testing/adjustments have been finalised.

3) Yep, understand what you say, a 20C differential is something being looked at, tested.

4) H/W priority is an interesting one and something being looked at.
- I will read up about parameter d.0


Thanks again for coming into the conversation.

Richard
 
The Heating System was designed and installed by the builder 'Persimmons'
I'm sure you appreciate that Persimmon would have sub-contracted the design and installation to a third-party, selected on the basis of who was the cheapest. You may be able to find, from the documentation provided with the house, who the actual installer was.

The energy consumption is from a status page of the mobile app that talks to the pump via bluetooth, it is not connected to what the boiler is consuming.
OK. I'll have to investigate this further

The boiler is set to 65c as was advised by Glowworm, we are looking at adjusting this.
Where did you get this info from? I hope the system designer took this into account!

I had a InfraRed Gun pointed at the steel panel of the radiator, about an inch in from the flow and return valves.
IR thermometers can give false readings as they depend on the emissivity of the material (shininess) they are pointed at. So a bright copper pipe will give a lower temperature reading than one which is oxidised. If the rad/pipe is painted the reading will be fairly accurate. It might be helpful to measure the temperature of the flow and return pipes where they enter the boiler . wrap some black insulation tape round the pipes if they are unpainted copper and point the IR gun at the tape.

Yep, understand what you say, a 20C differential is something being looked at, tested.
You may be able to achieve a higher differential by reducing the pump speed and opening the LS valves a little. It's trial and error.
 

Similar plumbing topics

Everything working fine on PP mode - thanks...
Replies
7
Views
914
Getting some progress on boiler room...
2 3 4 5
Replies
104
Views
12K
As below, the yellow or yellows flash, I...
2
Replies
37
Views
29K
Thanks Ric, Yeah I will go with what...
Replies
10
Views
6K
P
Mr Speaker: I'm tempted to draught a sarcastic...
Replies
22
Views
4K
Back
Top